I did a job where I have to run wiring from a rooftop solar array to the main circuit breaker box. Went to inspection and the inspector flagged me for using THHN and not THWN-2, citing that because of the heat on the roof, the internal temperature in the EMT could cause a problem with the insulation on the wiring. I'll buy that. He referred me 310.16, the temperature correction factor chart. He also referred me 3.15B-2c which he said deals with outside wiring. I can't find this chart in my 2005 code book, which I believe they are still using here in Maryland.
I have (12) 10 gauge + (1) 8 gauge (green) in 1" EMT with compression connectors
Now here's my central question. As I read 310.16 it states it's referring to 3 current conductors in per stick of EMT. Does this mean that I cant run more than 3 current carrying conductors per stick?