I understand it is not a safe practice to do so but is it a code violation to connect a 60deg Rated cable to a 75deg rated equipment lug? What could be the possible issues/outcomes in doing so?
That is a common situation and nothing will happen as long as the circuit ampacity is based on 60C.
The reason i ask is that some manufacturer documentations state clearly that - on a 75degree rated equipment lug, a 60degree rated cable cannot be used.
Can you be specific about the equipment?
It's a conservative approach to match terminal lug to element side lead insulation for terminal lug interfacing elements and equipment service entry. You would match or exceed line side insulation to instructions but it doesn't mean you have to run fiberglass insulated cable.There isn't a specific equipment that i have in mind. I was reviewing a Cable/Wire specification on a drawing which called out for the "equipment lugs to be equal to or exceed the cable temperature rating" which seemed to not match manufacturer recommendations. Hence the question.