James Williams
Member
- Location
- Fairmont, WV, USA
- Occupation
- Retired master electrician
I've got a UL listed 200A 1ø meter socket I will use in a feeder to an art studio building fed from my house. The feed will be #2 AL URD. It has a 100A rating at 90°C and I want to feed it from a 100A breaker.
The meter socket label is not marked with a temp rating for the terminals, and the terminals (ILSCO D3845) are not marked with a rating either. The cut sheet and instructions from Siemens have no temp rating listed. I googled and found several POCOs that specify 90°C as part of their meter socket specifications. Googling ILSCO D3845 produces no relevant response.
Is it OK to assume a 90°C rating?
I also assume that most everything POCO-related is 90°C anyway.
The meter socket label is not marked with a temp rating for the terminals, and the terminals (ILSCO D3845) are not marked with a rating either. The cut sheet and instructions from Siemens have no temp rating listed. I googled and found several POCOs that specify 90°C as part of their meter socket specifications. Googling ILSCO D3845 produces no relevant response.
Is it OK to assume a 90°C rating?
I also assume that most everything POCO-related is 90°C anyway.