Temperature rating of breaker

Status
Not open for further replies.

JohnJ0906

Senior Member
Location
Baltimore, MD
I had to check a residential loadcenter panel that had "warm breakers". I found 4 CH GFCI breakers in a row. I measured the temp at 34 deg. C. However, there was no temp rating on the breaker. I can't find anything in the Cutler Hammer info on the Eaton website. Does anyone know what the temp rating is?

I spread out the breakers to give some space for the heat to dissipate space-breaker-space, etc.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
JohnJ0906 said:
Zip. House is unoccupied, and lights were off, no loads plugged in.

I beleive the breakers had to have some load on them for any heat to be generated.

IIRC, most breakers are rated for an ambient temperature of 40 deg c.
 

mdshunk

Senior Member
Location
Right here.
34c is only 94 f. Considering that GFCI and AFCI breakers do have a bit of a temperature rise on their own, that doesn't seem too earth-shattering to me. What was the ambient when they were checked?
 

JohnJ0906

Senior Member
Location
Baltimore, MD
petersonra said:
I beleive the breakers had to have some load on them for any heat to be generated.

The GFCI breakers were noticably warmer to the touch than the standard breakers

"Cicuit breakers, the performance of which may be affected by a 40 deg. C. ambient temperature within the enclosure, and have been investigated for this application, are marked "40 deg. C." "
This is from the UL white book. I really wasn't sure what it meant :)roll: ), but these breakers had no marking, which prompted this question.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
mdshunk said:
34c is only 94 f. Considering that GFCI and AFCI breakers do have a bit of a temperature rise on their own, that doesn't seem too earth-shattering to me. What was the ambient when they were checked?

About 80 (It was MUCH warmer in the attic, but thats another issue :roll: )
 

mdshunk

Senior Member
Location
Right here.
I wonder if that information is on one of the white papers in a CH GFCI box? I don't have any trucks handy here at home to just go check, but I might have a GFCI white paper in a binder someplace...
 

mdshunk

Senior Member
Location
Right here.
JohnJ0906 said:
About 80 (It was MUCH warmer in the attic, but thats another issue :roll: )
Well... all this fussin' for a 14 degree F temperature rise? :grin: You did the right thing... spread them out and move on, never to think about it again.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
I couldn't find anything on the web site, and I checked several documents. Of course the instructions on the site and the ones in the box could be different.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
mdshunk said:
Well... all this fussin' for a 14 degree F temperature rise? :grin: You did the right thing... spread them out and move on, never to think about it again.

It was the lack of any temp rating that concerned me. I'm used to seeing a temp rating on everything. They were labeled "60/75 deg wire"

Also, as I said, this was with no load. I thought it would be a good idea to run it past all y'all.
 

davidr43229

Senior Member
Location
Columbus, Oh
Per UL489 standard Molded Case CB have a temp rating of 40 degrees C.
I would check the wire connections and make sure they are tight.
Also understand that with MCCB they have a trip rating of 1 time in a fault.
Multiple trips introduce carbon and pitting on the contacts.
It maybe time to replace that breaker.
Just my $.02
 

JohnJ0906

Senior Member
Location
Baltimore, MD
All connections tight. (1st thing I checked)
I removed all 4 breakers (to relocate) and none had the temp rating stamped on it, I even checked the bottom.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The UL standard for breakers permits a 50?C rise over the 40?C ambient for the internal parts. This would create a surface temperature that would burn you if you touched it for more than a few seconds. In this case with no load the temperature rise is from the electronics in the GFCI breakers.
Don
 

brian john

Senior Member
Location
Leesburg, VA
Totally of the subject, but for those use to USA standard of Fahrenheit a quick conversion in the lower temperatures (courtesy of my English relatives).

Take the Celsius temp times 2 and add 32, gets you in the ball park.

30C X 2 = 60 + 32 + 92F

30C X 1.8 = 54+ 32 = 86F

Would not use for any tight calculations but for quick reference it is usable.

This works best for quick conversions of daily temperatures, it gets way off at higher temperatures.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
For those who need a free program to convert temperatures as well as many other measurements you can go here and download one.
Don
 
You said that there was no current flow through any of the breakers, standard breakers having bimetal trip mechanisms only get warm when a current flows. The gfci has an internal power supply and an IC to measure current differance, these will produce heat, especiany when several GFCI's are placed together.
 