Temperature rating

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
What is the temperature rating of schedule 40 pvc ?.( 2011 code)
 
Code requires that PVC be listed, does not specify the requirements. As far as I know, all of it is listed for 90 degrees C, code limits it to installations were ambient is 50 degrees C or lower.
 
From Carlon Page 168:

Schedule 40 PVC Rigid Nonmetallic Conduit (RNC).
(Heavy Wall EPC)
Listed for underground applications encased in concrete or direct burial.Also for use in
exposed or concealed applications above ground.
• Sunlight resistant • Rated for use with 90˚C conductors • Superior weathering characteristics
 
PVC

PVC

Code requires that PVC be listed, does not specify the requirements. As far as I know, all of it is listed for 90 degrees C, code limits it to installations were ambient is 50 degrees C or lower.

PVC 50 degrees c ambient, rated for 90 c wire. help I do not understand. ( 50 c what article 2011 code )
 