Hi,
This is a two-part question concerning PV wire de-rating:
Q1) Let's say we're considering the wire run from the junction box attached to the rails, to the inverter which is mounted upright on the side of the house. Most of the wire is run through the attic in LFMC. There's a tiny portion of the conduit run in EMT from the j-box straight-down to the where it penetrates the roof. Let's say it's only a 5" distance.
Would the Rooftop Added Temperature Per Table 310.15(B)(3)(c) require me to include a temperature adder because of that 5" distance, or can I just bypass this since it's such a small part of the run, with most of it is in the attic?
Q2) I have often been confused on why THWN-2 is used in many PV installations, even though we are required to adhere to the 75 degree Celsius temperature terminal rating. Wouldn't it make more sense to just use 75-degree rated wire if we can't exceed the ampacity of the 75C column? Maybe I'm missing something.
Thanks in advance!
Regards,
Andy
This is a two-part question concerning PV wire de-rating:
Q1) Let's say we're considering the wire run from the junction box attached to the rails, to the inverter which is mounted upright on the side of the house. Most of the wire is run through the attic in LFMC. There's a tiny portion of the conduit run in EMT from the j-box straight-down to the where it penetrates the roof. Let's say it's only a 5" distance.
Would the Rooftop Added Temperature Per Table 310.15(B)(3)(c) require me to include a temperature adder because of that 5" distance, or can I just bypass this since it's such a small part of the run, with most of it is in the attic?
Q2) I have often been confused on why THWN-2 is used in many PV installations, even though we are required to adhere to the 75 degree Celsius temperature terminal rating. Wouldn't it make more sense to just use 75-degree rated wire if we can't exceed the ampacity of the 75C column? Maybe I'm missing something.
Thanks in advance!