- Location
- Illinois
- Occupation
- retired electrician
I have a temperature switch with 1/2" threaded conduit and 8" leads on one end. The other end of the switch has pipe thread and will be inserted into the process piping. The process fluid is water. The location where the switch will be installed is a Class I, Divison 2, Group D location.
This switch is not maked as suitable for the classification. The manufacturer says that if I install a conduit body suitable for the classification, make my splices in the conduit body and place a seal fitting on the other opening of the conduit body that I can use the switch in the classified area. Is the manufacturer correct? I believe that the switch itself must be marked as suitable for the classification.
Don
This switch is not maked as suitable for the classification. The manufacturer says that if I install a conduit body suitable for the classification, make my splices in the conduit body and place a seal fitting on the other opening of the conduit body that I can use the switch in the classified area. Is the manufacturer correct? I believe that the switch itself must be marked as suitable for the classification.
Don