I have 2 large 3 phase 480 volt motors needing to be wired up individually with SOOW cord but the NEC stops at #2 AWG at 80 amperes max before temperature derating adjustment.
The FLC ampacity of the motors require 124 amperes and wires are sized 1.25% of this for continuous duty = 155 ampere wire
Apparently SOOW is made larger than #2 but I can’t find a chart anywhere meeting or exceeding 155 amperes?
Where can I find specs for larger SOOW than #2? Thanks
The FLC ampacity of the motors require 124 amperes and wires are sized 1.25% of this for continuous duty = 155 ampere wire
Apparently SOOW is made larger than #2 but I can’t find a chart anywhere meeting or exceeding 155 amperes?
Where can I find specs for larger SOOW than #2? Thanks