Electrician is to replace a building's 800A SES and orders a temporary 1000W generator (that has a 3000A main circuit breaker) that he wants to hook up to the distribution panel to keep the building going while he replaces the SES. He wants to hook up the genset with (3) sets of 4/0 and a 4/0 GND. The City now wants me (the engineer) to draw up a plan showing fault current, etc. But to me, the 3000A gen breaker won't protect the 3 sets of 4/0 (although I realize that the generator will likely die if there is a short). How is this usually handled in a temporary situation? Surely they don't run 3000A worth of cable to a <800A load.