Anthony Giordano
Member
- Location
- Oakland, NJ
Hey all. I have a little difficult situation that I am dealing with, that I need some assistance with. I am doing a Chiller Replacement project in Albany, NY, where two (2) 500 Ton water cooled chillers are being replaced by two (2) new 500 Ton air cooled chillers. While the demolition and new construction is going on, a temporary 500 Ton air cooled rental chiller is being utilized for the plant. This chiller is dual circuit, with MCA's of 490A & 561A respectively. The recommended MOP's are 600A & 700A respectively.
In the double-ended Main-Tie-Main 480V 2000 KVA switchboard that feeds the plant, I only have one 1600AF circuit breaker with adjustable trip available to use to feed this temp chiller. I would like to use this single source 1600A C/B in order to feed the chiller, set the adjustable trip to 1200A, then have the temporary cables feed from one circuit breaker over to the other. Is this permissable?
The Trane rep. said the following in an email yesterday: In regards to the question about the power, am I clear in understanding that the customer wants to have a 1200 amp service break out into two separate 600 amp breakers prior to feeding our chiller? Or are they wanting to use a single 1200 amp source to provide power to our two separate ckts? I would be concerned that code would not allow a single 1200 amp source to provide power to two separate ckts, our recommendation would be to have a 600 Amp and 700 Amp Breaker(Sized for MOP) to feed the chiller. This would be up to electrical contractor and inspector though.
Thanks in advance for any feedback that I might receive on this thread.
In the double-ended Main-Tie-Main 480V 2000 KVA switchboard that feeds the plant, I only have one 1600AF circuit breaker with adjustable trip available to use to feed this temp chiller. I would like to use this single source 1600A C/B in order to feed the chiller, set the adjustable trip to 1200A, then have the temporary cables feed from one circuit breaker over to the other. Is this permissable?
The Trane rep. said the following in an email yesterday: In regards to the question about the power, am I clear in understanding that the customer wants to have a 1200 amp service break out into two separate 600 amp breakers prior to feeding our chiller? Or are they wanting to use a single 1200 amp source to provide power to our two separate ckts? I would be concerned that code would not allow a single 1200 amp source to provide power to two separate ckts, our recommendation would be to have a 600 Amp and 700 Amp Breaker(Sized for MOP) to feed the chiller. This would be up to electrical contractor and inspector though.
Thanks in advance for any feedback that I might receive on this thread.