It needs to be protected from damage, but not necessarily buried.
Sent from my XT1585 using Tapatalk
I agree. 590.3(C) allows temporary power and lighting during emergency's but 590.2(A) does not give any relief from article 700 and 590.2(B) would require approval of the installation.I don't have a code reference, but I don't believe the cables should not be accessible to the general public. (If you are running something like camlock cables.)
Does anyone agree, or disagree?
I don't have a code reference, but I don't believe the cables should not be accessible to the general public. (If you are running something like camlock cables.)
Does anyone agree, or disagree?
I don't have a code reference, but I don't believe the cables should not be accessible to the general public. (If you are running something like camlock cables.)
Does anyone agree, or disagree?
Life Safety would be an article 517 system, Emergency could be an article 517 or an article 700 system, and Standby (meaning Optional) would be a 700.2 system, the OP says it's for an emergency system.Interesting. Have not heard this. Looking forward to input on the subject. Brings up a Q: is this an emergency standby genset or a life safety genset?
Interesting. Have not heard this. Looking forward to input on the subject. Brings up a Q: is this an emergency standby genset or a life safety genset?
I believe anbm's past posts have often referred to hospitals.
So I was assuming this is a hospital generator, and that it probably supplies a mix of emergency, critical, and life safety loads.
I agree the rules would be a lot more lax for an optional generator. Are those cam-lock cables that Carnivals frequently just run across the ground, and everyone walks over them? If it's an optional generator, I don't think it would be much different.
Are those cam-lock cables that Carnivals frequently just run across the ground, and everyone walks over them? If it's an optional generator, I don't think it would be much different.
Life Safety would be an article 517 system, Emergency could be an article 517 or an article 700 system, and Standby (meaning Optional) would be a 700.2 system, the OP says it's for an emergency system.
If it is an optional standby system the rules would be a lot more lax.
Roger
The wiring methods are still covered elsewhere in the code.I'm glad you brought our attention to 590. Good add to the topic - one that I will look to more often now.
For our instance, new to the code in 2017 is 700.3(F) [typically accepted forward code cycle interpretation if jurisdiction is in an earlier code cycle]. This requires a temporary connection means, but does not outline anything beyond the need to have a connection point.
I'd say if your installation met wiring requirements covered elsewhere in the code you would be fine.I'd go so far as to say the code realizes an emergency condition does not warrant more then an electrically safe, not necessarily hardened, installation for a temporary installation needed to substitute emergency power.
Once again, 590 does not give any relief to the requirements of 700.10.Even still, if the AHJ required further, what kind of precautions must be made? 700 does not dictate type of wire/cable. The only item I see possibly is 1-hr rating a run for the occupancy conditions in 700.12.
Once again, 590 does not give any relief to the requirements of 700.10.
Now that the OP has clarified this is in a hospital 517.30(C)(3) ( 517.31(C)(3) in the 2017) could / would come into play.
The wiring methods are still covered elsewhere in the code.
I'd say if your installation met wiring requirements covered elsewhere in the code you would be fine.
Once again, 590 does not give any relief to the requirements of 700.10.
Now that the OP has clarified this is in a hospital 517.30(C)(3) ( 517.31(C)(3) in the 2017) could / would come into play.
Roger
See 700.10(C), (D)(1),(2), and(3)I do not see anything in 700.10 that would require cam lock cables to have anything special in a temporary installation.
I guess it would be up to the AHJ but in the hospitals I normally work in even temporary dust partitions must be built to a full UL recognized wall assembly and must be properly rated down to fire retardant framing members and backing if using wood.517.30C sure sounds like overkill for a temporary installation that may only be in place a few hours. I really never thought of that as being a requirement for a temp. installation.
I wonder if the AHJ could approve an installation without the conduit based on 590(B)?