Hi all,
I have a project in NJ where we need to run a temporary 480V, 300A, 4W+G feeder from a panel in the penthouse level down to the lower level of a 4 story building. The plan is to run this feeder out of the penthouse, along the rooftop, and then down the side of the building to the ground, and enter into the lower level mechanical room through an air intake grate. The client would like to run this temp feeder using an outdoor rated cable. Would a Type G multiconductor cord or Type W single conductor cords be suitable for this install?
Also, I know that raceways and cable on rooftops are subject to derating, I assume this also applies to temporary cables, but my understanding is that if the cable is supported 7/8" above the roof, it does not need to be derated further than what's required for the ambient temperature in the area.
Thanks,
Chris
I have a project in NJ where we need to run a temporary 480V, 300A, 4W+G feeder from a panel in the penthouse level down to the lower level of a 4 story building. The plan is to run this feeder out of the penthouse, along the rooftop, and then down the side of the building to the ground, and enter into the lower level mechanical room through an air intake grate. The client would like to run this temp feeder using an outdoor rated cable. Would a Type G multiconductor cord or Type W single conductor cords be suitable for this install?