I have a project where I am removing one transformer and installing a new one in a different location to accommodate a building that is getting larger. The transformer serves 4 meter centers which are not associated with the building expansion. Due to the routing of the primary and project phasing, we cannot get the new transformer up and running before the old transformer must be removed.
It was suggested that we use a portable generator temporarily to re-feed the existing meter centers. However, the service laterals (120Y/208) from the POCO transformer do not contain and equipment grounding conductor and they are long (between 150 and 450' each at 600A). Thus, If we use a generator to take the place of the POCO transformer, I interpret that the generator definitely WILL be a separately derived system and that we must make the system N/G bond at the generator per 250.20(D) and 250.30(1).
I want to know if anyone believes that it is permitted to NOT run an equipment grounding conductor in the meter center service laterals (which will temporarily become "feeders" from the generator) and make the system bond at the meter center.
Thanks
It was suggested that we use a portable generator temporarily to re-feed the existing meter centers. However, the service laterals (120Y/208) from the POCO transformer do not contain and equipment grounding conductor and they are long (between 150 and 450' each at 600A). Thus, If we use a generator to take the place of the POCO transformer, I interpret that the generator definitely WILL be a separately derived system and that we must make the system N/G bond at the generator per 250.20(D) and 250.30(1).
I want to know if anyone believes that it is permitted to NOT run an equipment grounding conductor in the meter center service laterals (which will temporarily become "feeders" from the generator) and make the system bond at the meter center.