tpd

Member
A trailer mounted generator supplying 480 volt for temporary power on a belt project is being used. The electricians tied cable in through a CGB and hard wired it instead of using a cord and plug connection. So now does this require an electrode?
 
A trailer mounted generator supplying 480 volt for temporary power on a belt project is being used. The electricians tied cable in through a CGB and hard wired it instead of using a cord and plug connection. So now does this require an electrode?

Read 250.34 (A) and (B) (2011)
 
Far more important than the electrode is the system bonding jumper. Without it, some one could get a fatal shock.
 