Temporary installations 590.4(g)

Status
Not open for further replies.

1life1impact

Member
Location
CA
Occupation
electrician
on construction sites...does this men that you can literally just splice 2 nonmetallic multiconductor cords and simply tape them up with electrical tape , rather than use a jbox? (As long as equipment grounding continuity is maintained)
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Yes.
Note that they added another exception (2) in the 2020 NEC to clarify a few other common practices on construction sites.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
on construction sites...does this men that you can literally just splice 2 nonmetallic multiconductor cords and simply tape them up with electrical tape , rather than use a jbox? (As long as equipment grounding continuity is maintained)
I would use wire nuts.

Roger
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Oh yeah I would assume wirenuts are involved.