I'm visiting one of my company's facilities for a turnaround; they've disassembled a boiler and are using a fan at the opening of the boiler to cool it down. The fan is plugged into a NEMA 4 receptacle, which is designated for use in Class 1 Division 2 Groups B, C, and D. The receptacle has this rating because the area is Class 1 Division 2. The fan has a general purpose cord, connected to a general purpose extension cord, connected to a 1 foot long cord that fits into the NEMA 4 receptacle. The portion of the 1 foot cord that plugs into the receptacle utilizes a twist lock system, and the other end is an ordinary plug; hence the connection to the general purpose extension cord. I don't think what they've done is permitted (to code), but the plant personnel said there is an exception in the NEC which allows the installation because it is temporary. I recall there being an exception for temporary installations, however not one that applied to Article 500, and upon inspection of 500, I saw no such exception. Some Questions:
Is there an exception for temporary installations in hazardous locations? - Where is it?
Where is the exception for general installations, or are there several exceptions in different places? - Are there actually no exceptions?
Since they're doing maintenance on a potential source that is a C1D2 location under normal conditions, is the area C1D1 while under maintenance?
Given the information provided, is the installation acceptable? If not, why not?
Thank you
Is there an exception for temporary installations in hazardous locations? - Where is it?
Where is the exception for general installations, or are there several exceptions in different places? - Are there actually no exceptions?
Since they're doing maintenance on a potential source that is a C1D2 location under normal conditions, is the area C1D1 while under maintenance?
Given the information provided, is the installation acceptable? If not, why not?
Thank you