Temporary Power Disconnecting Means

Status
Not open for further replies.

GWITT

Member
I Have Received A Request To Install Eleven 480 Volt 100 Amp Cord Caps Exiting 24 Inches Out The Bottom Of A Wireway Mounted 12 Ft A.f.f.. Will The Branch Breakers Located With In 50 Ft Serve As A Suitable Disconnecting Means, Or Should I Install A Combination Service Disconnect/pin And Sleeve Receptacle, That Does Not Allow Un Plugging Untill The Disconnect Has Been Turned Off? Thanks.
 
I Forgot To Mention In My Post There Will Be A 12 Ft Non-conductive Ladder Platform To Reach The Wireway.
 
I personally may make the cord and plug connections lower and more accessible, but I think you will be O.K. with the breakers as disconnects providing you install breaker lock offs.
 