Hello, Im planning on bringing temporary power to a tiny house mounted on a metal trailer frame from a generator. Few questions, Would the best insulation for the supply cable be SOOW?
OK with approved cords that meet suitability.
Im planning on driving ground rods at the generator and at the tiny house with #6 bare copper. Should i bond to the frame of the trailer with an insulated #6 as well?
Since this is a temporary setup you are only required to make grounding provision at the generator unit up to line side of the disconnect. . . never at the load side. (NEC 551-16)
Lastly, the nueutral and ground busses should still be boned at the panel for the tiny house correct?
No, the neutral should not be bonded to the frame. If the neutral bus is bonded to the metal enclosure of the distribution panel, the bonding wire should be removed along with any pigtails in the branch circuits. (if there is any.) (NEC 551-24 .)
I suggest you peruse Art. 551 that covers mobile homes.