I need to setup temp power at a Industrial site for a 3 week shut down, I just need power for barge lights that have to be on 24/7 and a receptacle so we have power for temp lighting/tools, no more than 20Amps worth.
The existing transformer that feeds the panel for the barge lights is 45KVA 480v Delta to 208Y/120v, now my question is; If I ran 50A SO cord 500' with a 20A OCPD because of Voltage drop, will the Transformer still function properly and give me the 208Y/120v? or will I be running into issues like the OCPD tripping due to heat over load/ In rush current from trying to draw in 45KVA?
Thank you for all answers and insight you have to offer.
The existing transformer that feeds the panel for the barge lights is 45KVA 480v Delta to 208Y/120v, now my question is; If I ran 50A SO cord 500' with a 20A OCPD because of Voltage drop, will the Transformer still function properly and give me the 208Y/120v? or will I be running into issues like the OCPD tripping due to heat over load/ In rush current from trying to draw in 45KVA?