Temporary Trailer hook up

Status
Not open for further replies.

arnettda

Senior Member
I have a construction trailer to supply temporary power to. What does one usually do? I was looking at using 6/4 SOW cord to supply the trailer from the temp service 30 feet away. The ground is still froze so I can not dig anything in. The thing that scares me is having the wire lay ontop of the ground. It is somewhere people might walk over it. I am worried about someone getting hurt. And do I need to use SOW cord could i use U/F since it is a temp situation.
Thanks
 

iwire

Moderator
Staff member
Location
Massachusetts
If I could not go under and I could not go overhead I would likely run SER sleeved in schedule 80 PVC, this of course assumes only foot traffic no vehicles.
 

kbsparky

Senior Member
Location
Delmarva, USA
What's wrong with SOW cord? That stuff is heavy-duty rated, and perfect for such an application.

Easily moved around during construction, etc.

Put in a NEMA 14-50 receptacle outlet, and plug it in, just like the old trailer parks used to have!
 

iwire

Moderator
Staff member
Location
Massachusetts
What's wrong with SOW cord? That stuff is heavy-duty rated, and perfect for such an application.

Easily moved around during construction, etc.

Put in a NEMA 14-50 receptacle outlet, and plug it in, just like the old trailer parks used to have!

Nothing is wrong with it as long as you enjoy spending lots of money. That 14-50 will add to the cos as well.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
This is definitely a case where I'd check with the AHJ. Way too many variables, distance, amount of traffic, time in use, etc.
I;ve seen jobs where job trailers were required to be 100% NEC..buried conduit, etc, and jobs with "sleeved" cords, sleeved SE, etc., exposed rigid..the whole, gambit.
Oh, and "frozen ground" normally doesn't mean mcuh to inspectors, we don't dig:).
 

luckyshadow

Senior Member
Location
Maryland
In my neck of the woods SER is not allowed for this installation.

Article 550.4 (A) - Lists contractors onsite offices , and tells you that you must meet all requirements of the article
550.16 (B) supply cord OR Permanent Feeder - calls for an insulated grounding wire.

Going the distance you mention it can not be just laid on the ground either. It must be protected to keep it from being damaged thus protecting the people on the job site.
 