Temporary Wiring in Construction & Power lines

Status
Not open for further replies.

tex

Member
Finally - some electrical guru's I can count on.
I am a Safety Mgr for a GC. I have 3 questions:

1) Can temporary lights be plugged into a temporary gfci receptacle i.e. spider box? 1993 -NEC Reference Article 305-4(d)

2) Some electrical subs like to use romex for temporary wiring of lights and receptacles. I have noticed that they are putting cord caps (plug ends) on the romex to plug in to temporary receptacles. Are cord caps allowed to be installed on romex wiring for temporary purposes? Is this a UL thing with the Mfg. of cord caps?

3) Is it permissible to allow cranes or aerial lifts to work within 10' of powerlines rated at <50kv if the lines are sleeved with rated hose type covers as long as direct contact is avoided?

Thanks in advance for your input.
 

gregoryfast

Member
Location
Alaska
Re: Temporary Wiring in Construction & Power lines

OK, I'll give it my best shot.

1. Not a good idea, but I think it is permissable. I have seen a number of jobs where the spider trips and everyone is in the dark.

2. I have seen this mess also. It doesn't meet NEC nor OSHA regs. OSHA tends to overlook it as long as there is no contact with the building steel. The wire must be hung with an insulated method.

3. 10' is the maximum distance, covered or uncovered.
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Temporary Wiring in Construction & Power lines

1) NO
2) NO

2002 NEC
527.4(D) Receptacles. All receptacles shall be of the grounding type. Unless installed in a continuous grounded metal raceway or metal-covered cable, all branch circuits shall contain a separate equipment grounding conductor, and all receptacles shall be electrically connected to the equipment grounding conductors. Receptacles on construction sites shall not be installed on branch circuits that supply temporary lighting. Receptacles shall not be connected to the same ungrounded conductor of multiwire circuits that supply temporary lighting.

110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Temporary Wiring in Construction & Power lines

Originally posted by tex:
1) Can temporary lights be plugged into a temporary gfci receptacle i.e. spider box? 1993 -NEC Reference Article 305-4(d)
Not enough info here, are we talking about a portable light or a string of temps hung up?

A temp light stand yes.

Does a spider box have it's own individual branch circuit protection for the outlets on it?

If it does I would have to say you could power a temp light stings from the outlets.

Originally posted by tex:
2) Some electrical subs like to use romex for temporary wiring of lights and receptacles. I have noticed that they are putting cord caps (plug ends) on the romex to plug in to temporary receptacles. Are cord caps allowed to be installed on romex wiring for temporary purposes? Is this a UL thing with the Mfg. of cord caps?
NM is permitted for temps by NEC 527.4(C) and therefore also by OHSA

The cord caps I would say are a violation, article 527 does not relieve you from 110.3(B) as Dave pointed out. (Use as Directed)


Originally posted by TeX:
3) Is it permissible to allow cranes or aerial lifts to work within 10' of powerlines rated at <50kv if the lines are sleeved with rated hose type covers as long as direct contact is avoided?
This last one is just a guess.

From operating aerial lifts quite a bit and reading the safety instructions I would have to say no, it says do not operate near power lines, no mention of insulated or not.

[ November 18, 2003, 06:53 PM: Message edited by: iwire ]
 

ryan_618

Senior Member
Re: Temporary Wiring in Construction & Power lines

I would say that if the temporary lights are designed to be a cord and plug assembly, you must plug them into a GFCI receptacle outlet, as all receptacle outlets are be GFCI protected.
 

goodcode

Member
Re: Temporary Wiring in Construction & Power lines

1) Yes. Provided the temporary light stringer or lamp is provided with a male cord cap or the cord is of a type listed in Article 400 of the NEC as hard or extra hard usage cord. Note that a branch circuit serving temporary lighting is not permitted to serve other loads. See 29 CFR 1926.405(a)(2)(ii)(C) and 1926.403(b)(2).

2) Type NM, "romex" is permitted. Cord caps on type NM is prohibited. See 1926.403(b)(2).

3) Only where the lines are deenergized and visibly grounded or where insulating barriers are installed. Note that when this second method is utilized, grounding of the crane is required and an engineer with the utility must determine induced voltages and the specific installation. The following is a letter of interpretation from OSHA on this section discussing "insulating barriers." Note that the preferred method is the goal post type barrier.


February 8, 1994

Mr. Ivan Blood
St. Paul Five and Marine Insurance Company
500 W. Madison, Suite 2600
Chicago, Illinois 60661-2594


Dear Mr. Blood:

This is in response to your October 13 letter requesting an interpretation of an Occupational Safety and Health Administration (OSHA) standard addressing the operation of a crane in close proximity to overhead power lines. I apologize for the delay in responding to your inquiry.

With regard to what is acceptable as insulating barriers to prevent physical contact of equipment or machinery with electric distribution and transmission lines when the equipment or machinery is operating within 10 feet of the power lines, please be advised as follows: Rubber insulating equipment meeting the requirements of 29 CFR 1910.137 is normally intended as protection from "brushing" type contact for employees working on the lines. Although 1910.137 is not applicable to construction work, it may be used as a compliance guide for barriers required under the exception to 1926.550(a)(15), under certain conditions. If hard direct contact with the line is not likely, rubber insulating equipment can provide protection from brush contact with the power line. However, if direct impact with the lines is reasonably likely or expected, this equipment will not provide the necessary protection. In such cases, other types of barriers would be required, such as those listed in the National Safety Council Data Sheet No. 1-743New90 and the types of plastic guard equipment covered in ASTM F968, Specification for Electrically Insulating Plastic Guard Equipment for Protection of Workers. Although guards of a type consisting of ABS plastic, 1/8-inch thick, (approximate puncture strength 50,000 volts) are often successfully used on 15KV and 34.5KV systems, none are totally impact proof to the extent that strong direct blows would leave the air gap integrity unchanged or not cause sliding or other adverse movement along the line.

While the "goal post" type of guarding approach to overhead line safety probably provides the most durable means of withstanding barrier impact, it should be remembered that no practical barrier can absolutely prevent contact of a crane (or similar material handling device), simply because the capabilities of such heavy operating devices normally overwhelm any obstruction that may be installed.

If we can be of any further assistance please contact me or Dale Cavanaugh of my staff at (202) 219-8124.

Sincerely,


Roy F. Gurnham, P.E., J.D.
Director
Office of Construction and Maritime
Compliance Assistance
 

charlie

Senior Member
Location
Indianapolis
Re: Temporary Wiring in Construction & Power lines

My company refuses to cover lines for construction. We will de-energize and ground lines or drop lines for construction but will not cover lines. We have seen crane operators "brush" so hard on the line hoses that a fault occurs. If we don't cover up, they will wait for us to ground or drop.
 

tex

Member
Re: Temporary Wiring in Construction & Power lines

Thanks guys. Seems there is some differing opinions. The lights are temp light stringers.