M MichaelJ Member Location Georgia Dec 3, 2010 #1 I Would like to get everybodys opinion, Is Tray Cable type TC-ER approved for Temporary wiring for feeders to a sub panel? Cable is just strung thru steel purlins.
I Would like to get everybodys opinion, Is Tray Cable type TC-ER approved for Temporary wiring for feeders to a sub panel? Cable is just strung thru steel purlins.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Dec 3, 2010 #2 What about this? 336.12 Uses Not Permitted. Type TC tray cable shall not be installed or used as follows: (2) Installed outside a raceway or cable tray system, except as permitted in 336.10(7)
What about this? 336.12 Uses Not Permitted. Type TC tray cable shall not be installed or used as follows: (2) Installed outside a raceway or cable tray system, except as permitted in 336.10(7)