We have installed HPS fixtures in a metal building, no more than 7 fixtures per circuit, fixtures drawing 2 amps each, and the home run has 6 conductorss, w/ 1 ground wire.
The Inspector has determined that the heat that this building will see in the summer time, will be in the 140 to 160 degree area, and wants us to replace the #12 wiring with #10.
This building has the normal air turbines as well as power ventalitaion.This build is built with galv material which has has refelcted properties.
My calcuations at worst have me with derated wire and assuming no more than 120 degrees that this building would see, we show that the number 12's still are acceptable.
Anyone have insight to this ?
The Inspector has determined that the heat that this building will see in the summer time, will be in the 140 to 160 degree area, and wants us to replace the #12 wiring with #10.
This building has the normal air turbines as well as power ventalitaion.This build is built with galv material which has has refelcted properties.
My calcuations at worst have me with derated wire and assuming no more than 120 degrees that this building would see, we show that the number 12's still are acceptable.
Anyone have insight to this ?