We have a project where there is a 1200A meter enclosure with 5 meters; each at 200A. It is located on the outside on the end of a strip mall. There are 4 units each separated by a fire wall. We are correcting an incorrect installation so the current configuration is not a factor. 2 of the units have two (2) 200A services. When done, the load will not increase. We are going to remove the (2) 200A services from the 2 units and install a single 400A service into each of these. Now, my question on the metering setup. Right now, there are 5 meters in the enclosure each with their own breaker. Because the enclosures are only good for 200A meters, we need to add on an additional section for (2) 400A meters. Once done, unless we remove an existing section, there will be (2) 400A meters, (2) 200A meters, (3) blanked off sections. Breakers still add up to not exceeding 1200A rating.
First, keeping with the 6-disconnect rule, do the blanked off spaces come into the equation since the breaker is there but no meter? Next, what is somebody sees down the road they can add on and there are (3) 200A slots available. Now the potential exits for exceeding the 6 disconnect rule and exceeding the enclosure ampacity.
So do we remove 1 existing section and replace with 400A section so meter count does not exceed 6 or keep the section blanked off expecting the next person to check the NEC prior to adding on?
First, keeping with the 6-disconnect rule, do the blanked off spaces come into the equation since the breaker is there but no meter? Next, what is somebody sees down the road they can add on and there are (3) 200A slots available. Now the potential exits for exceeding the 6 disconnect rule and exceeding the enclosure ampacity.
So do we remove 1 existing section and replace with 400A section so meter count does not exceed 6 or keep the section blanked off expecting the next person to check the NEC prior to adding on?