I have a question; the installation is using #12 AWG type THWN-2 copper conductors and the terminations are rated 60 degrees C. There are six current carrying conductors, in 3/4" conduit, running through an attic with an ambient temperature of 132 degrees F. The load on the conductors is 16A non-continuous.
My calculations are as follows:
[FONT=Swis721 BT, sans-serif]Conductor sizing calculations[/FONT]
[FONT=Swis721 BT, sans-serif]12 AWG THWN-2 (90 degree C) = 30A[/FONT]
[FONT=Swis721 BT, sans-serif]For six current carrying conductors derate 80%[/FONT]
[FONT=Swis721 BT, sans-serif]30A x 0.8 = 24A[/FONT]
[FONT=Swis721 BT, sans-serif]for ambient temperature of 132oF derate 71%[/FONT]
[FONT=Swis721 BT, sans-serif]24A x 0.71 = 17A[/FONT]
[FONT=Swis721 BT, sans-serif]The load is 16A, 12 AWG at 60oC is rated 20A the OCPD is rated 20A[/FONT]
[FONT=Swis721 BT, sans-serif]The conductors are appropriate for the application. Correct?[/FONT]