If the electrical contractor installs terminal blocks within JB's inside an electrical room, do they have to have a field inspection for approval for UL50? This is an industrial waste treatment plant.
Some are listed, but most are recognized....I just chose to ignore that issue when I assemble a terminal boxBut, the din rail terminal blocks are ul component recognized, not listed. There are listed terminal strips
But field install of terminal blocks is very common.
True, but the OP never said they were DIN rail terminals.But, the din rail terminal blocks are ul component recognized, not listed. There are listed terminal strips
But field install of terminal blocks is very common.
And strangely, the terminal blocks behave exactly the same, whether or not their installation has been ble$$ed by the high priests at UL.Some are listed, but most are recognized....I just chose to ignore that issue when I assemble a terminal box![]()