Terminal Box

Status
Not open for further replies.

dnbob

Senior Member
Location
Rochester, MN
When setting a terminal box after the utility meter, isn't over current protection required at that point? Seems there was a different article, but seems 230.90 would require it.
What they want to do is feed the 200 amp service on the house, and then extend an additional 100 amp service to a detached garage/shop.

Thanks,

Bob
 
When setting a terminal box after the utility meter, isn't over current protection required at that point? Seems there was a different article, but seems 230.90 would require it.
What they want to do is feed the 200 amp service on the house, and then extend an additional 100 amp service to a detached garage/shop.

Thanks,

Bob

Take a look at 230.40 Ex. #3
 