In Mike Holt's Grounding and Bonding book, there is an Author's Comment regarding to the sizing of the equipment grounding conductor. For those who have the book,it is on page 64.
It bascially states Table 250.122 may not be good enough if the available ground-fault current is so high that it effects the contact resistance of terminations. He then provides a table with breaker ratings and multipliers.
An example is also provided. After the calculation is made and the multiplier is used, the equipment grounding conductor is larger than required by Table 250.122.
Where did these multiplier values come from, and why is this not specified in the code?
It bascially states Table 250.122 may not be good enough if the available ground-fault current is so high that it effects the contact resistance of terminations. He then provides a table with breaker ratings and multipliers.
An example is also provided. After the calculation is made and the multiplier is used, the equipment grounding conductor is larger than required by Table 250.122.
Where did these multiplier values come from, and why is this not specified in the code?