I need help to understand the terminal limitations code requirement.
Example of situation:
You have 75C terminal which is panel and the load spec says to use 90C copper, (4) conductor of 6AWG and (1) 10AWG Ground.
Table 310.16 under 90C, 6AWG is 75A
So does that mean I need 4AWG in 75C column?
Thanks for the support!