Terminal Listing

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
At a CEU seminar the speaker stated that this terminal when used with two conductors were permitted to be used only to terminate parallel conductors and therefore are only permitted with conductors that are the same size as part of the listing. Has anyone ever heard of those two requirements when landing two conductors?

Two Wire Terminal.JPG
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I've seen that requirement more than once where you can have two wires on the terminal as long as they're the same size and both are stranded or both are solid. I we'll see if I can find such a terminal. Of course now that I've opened my big mouth about it I won't be able to find one with that kind of restriction.
 

Carultch

Senior Member
Location
Massachusetts
I've seen that requirement more than once where you can have two wires on the terminal as long as they're the same size and both are stranded or both are solid. I we'll see if I can find such a terminal. Of course now that I've opened my big mouth about it I won't be able to find one with that kind of restriction.

Here's an example where it explicitly states "No mixing wire gauges":

This doesn't necessarily mean that you could only use this for conductors in parallel, just that you could only use it for two conductors of the same size.

I have asked Square D about the "snowman" lugs they use on the 400A disconnects, and whether it was permitted to mix sizes in the two-wire range within the same barrel, and the answer was that it was permitted. Just not allowed to mix aluminum and copper in the same barrel (which I expect), even though the lug is rated for use with wire of either metal.
 
Last edited:
D

Dell3c

Guest
Well, welcome to the 21st century.
Noticing having two(2) 1/0 conductors (together) under same lug (hole). I remember @ one time, must use lug having (tear-drop type hole) being the only mechanical lug acceptable for "more than one conductor" in same lug hole.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Well, welcome to the 21st century.
Noticing having two(2) 1/0 conductors (together) under same lug (hole). I remember @ one time, must use lug having (tear-drop type hole) being the only mechanical lug acceptable for "more than one conductor" in same lug hole.
Not visible from the photo but that is a tear drop shaped hole in the terminal.
 
D

Dell3c

Guest
infinity.. Open link in post #6, the third window in the link. Click on lug (expand) w/two 1/0 conductors. in same hole.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
This kinda thing is why the code should contain 'construction specifications' for something as simple as a lug and not require them to be listed.
There are ongoing efforts to make every nut, bolt, screw and ziptie you all use to be 'listed'.
 
Status
Not open for further replies.
Top