Is the 350MCM-6 saying I can use 350MCM down to a 6 gauge in this terminal ?
SG-1 Senior Member Location Ware Shoals, South Carolina Jun 16, 2011 #1 Is the 350MCM-6 saying I can use 350MCM down to a 6 gauge in this terminal ?
iwire Moderator Staff member Location Massachusetts Jun 16, 2011 #2 SG-1 said: View attachment 5517 Is the 350MCM-6 saying I can use 350MCM down to a 6 gauge in this terminal ? Click to expand... Yes, but as a side note I doubt that terminal is listed for use with the fine stranded conductor in the picture.
SG-1 said: View attachment 5517 Is the 350MCM-6 saying I can use 350MCM down to a 6 gauge in this terminal ? Click to expand... Yes, but as a side note I doubt that terminal is listed for use with the fine stranded conductor in the picture.
SG-1 Senior Member Location Ware Shoals, South Carolina Jun 16, 2011 #4 Thanks iwire, I agree the terminal is not approved for the conductor. That is a fight I cannot win on this one.
Thanks iwire, I agree the terminal is not approved for the conductor. That is a fight I cannot win on this one.