Hello everyone,
Is it correct to say if the equipment is rated over 600Volts, the conductor can be sized per 90 degree C regardless of the terminal rating. I am a little confused about NEC 110.40Conductors shall be permitted to be terminated based on the 90 °C (194 °F) temperature rating and ampacity as given in Table 310.60(C)(67) through Table 310.60(C)(86), unless otherwise identified.”
Also, NEC 110.40 is for voltage rating over 600 volts, however Table 310.60(c)(67)to(86) are for cables over 2000 volts, aren't we supposed to use 310.15.(B).(16) instead to size cables up to 2000volts?
Thanks everyone!
Is it correct to say if the equipment is rated over 600Volts, the conductor can be sized per 90 degree C regardless of the terminal rating. I am a little confused about NEC 110.40Conductors shall be permitted to be terminated based on the 90 °C (194 °F) temperature rating and ampacity as given in Table 310.60(C)(67) through Table 310.60(C)(86), unless otherwise identified.”
Also, NEC 110.40 is for voltage rating over 600 volts, however Table 310.60(c)(67)to(86) are for cables over 2000 volts, aren't we supposed to use 310.15.(B).(16) instead to size cables up to 2000volts?