Hey all
I am coaching a student who is preparing to sit for the California electrician certification. My student is using Tom and Tim Henry's 2017 Exam Questions and Answers. The relevant question (and this issue crops up time and again in their other questions) is question number three on the chapter two, end of chapter test on page 59. The query is: " The ampacity of copper # 10 THWN-2 is ____ when there are three current carrying conductors in the conduit and the ambient temperature is 70 degrees F.
Their answer here and in many other instances, assumes a terminal temperature rating based on the insulation. In this case that would be the 90 degree C column. I referred my student to 110.14 C (1) (a) (3). As I have understood this for years, it means that unless a higher terminal temperature rating is indicated on both ends of the termination, one must begin with the 60 degree column and can only use the 90 degree column when adjusting for conduit fill and ambient temperature adjustments. The Henrys, in this case and in other instances in their book, default to the 90 degree column for a starting point.
Anybody care to comment? Have I been doing this wrong for the past 400 years?
I am coaching a student who is preparing to sit for the California electrician certification. My student is using Tom and Tim Henry's 2017 Exam Questions and Answers. The relevant question (and this issue crops up time and again in their other questions) is question number three on the chapter two, end of chapter test on page 59. The query is: " The ampacity of copper # 10 THWN-2 is ____ when there are three current carrying conductors in the conduit and the ambient temperature is 70 degrees F.
Their answer here and in many other instances, assumes a terminal temperature rating based on the insulation. In this case that would be the 90 degree C column. I referred my student to 110.14 C (1) (a) (3). As I have understood this for years, it means that unless a higher terminal temperature rating is indicated on both ends of the termination, one must begin with the 60 degree column and can only use the 90 degree column when adjusting for conduit fill and ambient temperature adjustments. The Henrys, in this case and in other instances in their book, default to the 90 degree column for a starting point.
Anybody care to comment? Have I been doing this wrong for the past 400 years?