Terminal Tempiture Rating

Status
Not open for further replies.

r.stevens

New member
Where is the best resource for finding the terminal temperature rating of devises? I have researched at manufactures web sites such as Leviton for data on their outlets to no avail. I always seem to have a problem finding "Listed" or "Labeled" information for equipment or devises. Where is the best source?
 
The UL White book will give you the requirements that equipment must meet in order to be "listed". For example, to be listed the terminations on a piece of equipment rated at 100 amps or less must be rated at 60-degrees. So unless the terminal is labeled otherwise, it will be rated at 60-degrees per the UL Listing. If it is suitable for higher temperatures, the terminal itself should be marked or there will be a label in the equipment giving the higher termination ratings.
 