This has been discussed at length here before, and as expected, opinions vary widely. Yes, it's perfectly legal to use stranded on screw terminals.can #12 stranded wire be used on a binding post of a receptical and where in the code does it list it
I'd always terminate the wire with a compression type lug.I find pinching the loop closed with needle-nose pliers while tightening the screw works just fine. Back-wired clamp-type terminals are the best bet.
You mean like a StaKon?I'd always terminate the wire with a compression type lug.
If the device is UL listed it must accept stranded wire.can #12 stranded wire be used on a binding post of a receptical and where in the code does it list it
Terminals of the wire-binding screw, setscrew, or screw-actuated back wired clamping types are suitable for use with both solid and stranded building wires.
I'm not familiar with Sta Kon products.You mean like a StaKon?
StaKon is a brand name, from Thomas & Betts, for the devices you pictured.I'm not familiar with Sta Kon products.
Dem's de ones.This for kind of thing small wiring:
I've always wondered whether it's "stake on" or "stay con(nected)".StaKon is a brand name, from Thomas & Betts, for the devices you pictured.
I'm not familiar with Sta Kon products.
This for kind of thing small wiring:
For larger conductors we use compression lugs like these and sleeve them with heatshrink to identify phases.
I always thought STAy KONnected.I've always wondered whether it's "stake on" or "stay con(nected)".
Many we use are also suitable for bare wire.Most all devices that I am aware of are listed as suitable for stranded conductors.