nollij
Member
- Location
- Washington
This is kind of a complicated situation so I will explain it the best that I can.
We are doing a replacement in kind of cable to a very large amount of motors. Recently the inspector notified us that we needed to seal the cable as these motors are in a classified area (Class 1 Division 2).
From my understanding, 501.15(E)(3) states that we do not need seals as we are not terminating at an enclosure required to be explosionproof (article 501.15(E)(1)) or terminating at a pressurized location.
Our I/E inspector said that article 501.15(E)(1) exception no. 1 implies that we need a cable seal at the boundary. I believe that the scope of 501.15(E)(1) only applies to terminations and that the exception does not expand the scope of the section (probably just poorly worded).
I am currently trying to get the manufacturer to provide information to apply 501.15(E)(2) so that we can just avoid this entire mess.
Section 501.15(B)(2) exception no. 2 was also brought up. Does this imply that a conduit seal is required if the cable is routed in tray all the way back to a substation and then into conduit, even if the conduit is not at the boundary? This exception is vague on what part of the routing the boundary crossing is and thus makes an implication that even if the conduit routing is not across the boundary, a seal is still required.
Thanks.
We are doing a replacement in kind of cable to a very large amount of motors. Recently the inspector notified us that we needed to seal the cable as these motors are in a classified area (Class 1 Division 2).
From my understanding, 501.15(E)(3) states that we do not need seals as we are not terminating at an enclosure required to be explosionproof (article 501.15(E)(1)) or terminating at a pressurized location.
Our I/E inspector said that article 501.15(E)(1) exception no. 1 implies that we need a cable seal at the boundary. I believe that the scope of 501.15(E)(1) only applies to terminations and that the exception does not expand the scope of the section (probably just poorly worded).
I am currently trying to get the manufacturer to provide information to apply 501.15(E)(2) so that we can just avoid this entire mess.
Section 501.15(B)(2) exception no. 2 was also brought up. Does this imply that a conduit seal is required if the cable is routed in tray all the way back to a substation and then into conduit, even if the conduit is not at the boundary? This exception is vague on what part of the routing the boundary crossing is and thus makes an implication that even if the conduit routing is not across the boundary, a seal is still required.
Thanks.