Does the EGC routed with the feeder conductors to a panel have to be terminated at the equipment ground bar or can it be terminated to a lug that is adequately attached to the panel itself say via machine screw and nut?
Scenario is oversized EGC routed with feeder conductors that is too big for the equipment ground bar. I would think that I can install a one hole lug and fasten to panel as above. 408.40 tells me that the only time that the EGC with the feeder conductors needs to be connected to the equipment ground bar is if panel is non metallic. Not the case here. This leads me to believe that connecting the feeder EGC to the metal of the panel would be acceptable. Am I looking at this correctly?
Scenario is oversized EGC routed with feeder conductors that is too big for the equipment ground bar. I would think that I can install a one hole lug and fasten to panel as above. 408.40 tells me that the only time that the EGC with the feeder conductors needs to be connected to the equipment ground bar is if panel is non metallic. Not the case here. This leads me to believe that connecting the feeder EGC to the metal of the panel would be acceptable. Am I looking at this correctly?