I need some help on how to terminate the GEC in a two unit dwelling.
Please see my crude drawing attached.
View attachment 763
Typically, I have seen this done this way:
1) GEC hits rods and water pipes (one continuous conductor),
2) enters the meter socket (no bonding bushing, this conductor is not in a raceway)
3) GEC hits a bonding bushing on each of three nipples,
4) then ends at the neutral bus in the meter socket.
One inspector is saying this is o.k., the other inspector is saying that the GEC needs to continue through to the CB panels because those include the service disconnects.
If this is true, that the GEC needs to continue to the CB panels, how do I accomplish this? Do I add a small bus in the meter socket and bond it to the enclosure and then therminate the GEC there and then run additional condutors from the bus in the meter socket to the neutral bus in each CB panel?
OR, do I make an enclosure just below the meter socket, terminate the GEC to a bus there, and then run conductors to each CB panel neutral bus?
I don't own large crimping equipment and I haven't been able to find a place to rent it locally. I believe that the ideal solution would be to tap the GEC below the meter socket with suitable crimp connectors and then run a tap to each CB panel (skipping the meter socket altogether).
Thanks for your help.
Please see my crude drawing attached.
View attachment 763
Typically, I have seen this done this way:
1) GEC hits rods and water pipes (one continuous conductor),
2) enters the meter socket (no bonding bushing, this conductor is not in a raceway)
3) GEC hits a bonding bushing on each of three nipples,
4) then ends at the neutral bus in the meter socket.
One inspector is saying this is o.k., the other inspector is saying that the GEC needs to continue through to the CB panels because those include the service disconnects.
If this is true, that the GEC needs to continue to the CB panels, how do I accomplish this? Do I add a small bus in the meter socket and bond it to the enclosure and then therminate the GEC there and then run additional condutors from the bus in the meter socket to the neutral bus in each CB panel?
OR, do I make an enclosure just below the meter socket, terminate the GEC to a bus there, and then run conductors to each CB panel neutral bus?
I don't own large crimping equipment and I haven't been able to find a place to rent it locally. I believe that the ideal solution would be to tap the GEC below the meter socket with suitable crimp connectors and then run a tap to each CB panel (skipping the meter socket altogether).
Thanks for your help.