A Alwayslearningelec Senior Member Location NJ Occupation Estimator Aug 10, 2023 #1 I'm being asked to run a 2" RGS conduit w/ 4#1/0 and #6 from this panel? It looks pretty crowded. Do you see any issues? Attachments Screenshot 2023-08-10 115101.jpg 184.7 KB · Views: 25 Screenshot 2023-08-10 115121.jpg 138 KB · Views: 25 Screenshot 2023-08-10 115531.jpg 22.8 KB · Views: 25
I'm being asked to run a 2" RGS conduit w/ 4#1/0 and #6 from this panel? It looks pretty crowded. Do you see any issues?
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Aug 10, 2023 #2 Have you verified there is actually space on top to put in another conduit of the size required? If not you might have to put some kind of a gutter or wire way on the side and run the conduit to that.
Have you verified there is actually space on top to put in another conduit of the size required? If not you might have to put some kind of a gutter or wire way on the side and run the conduit to that.