J. Hofstetter
- Berne, Indiana, USA
I am putting together a sand and gravel plant that is stretched out over a pretty long distance. A couple of the conveyor motors are reaching out to 1500' from the MCC. We've done all the calculations to compensate for voltage drop which has increased the wire significantly from what it would be if the motors were within any reasonable distance. Now it's time for terminating the motor leads. I was taught a long time ago that the first few feet from the motor starter and the last few feet to the motor that I could size the wire to the load without concern for voltage drop, which is pretty handy because most generally you can't fit the oversized motor leads in the motor starter lugs without cutting few stands off. This has always worked with no issues, but what is the actual code rule that allows this (if any)?
Thanks,
Thanks,