Saw a job done by a Craigslist "electrician"... :rant:
A sub installed next to the service panel.
All the homeruns originate through the main panel knockouts.
Only the ungrounded conductors were brought from the main into the sub, through a short EMT nipple, and terminated at the breakers in the sub.
All the neturals were terminated in the main, effectively in a different panel from where the ungrounded conductors originate.
I know it is wrong, but I can't come up with the proper code reference.
300-3 (b) does not refer to a panelboard -- only to "raceway, cable tray, trench, cable, or cord"
210.4 AFAIK is only about MWBC's, but not every circuit is an MWBC.
Any thoughts?