Got red tagged for taping the ends of some old wires instead of using wire nuts. What code says that tape alone is not a proper termination?
Got red tagged for taping the ends of some old wires instead of using wire nuts. What code says that tape alone is not a proper termination?
Seems a bit harsh.Got red tagged for taping the ends of some old wires instead of using wire nuts. What code says that tape alone is not a proper termination?
Fair point.I use tape all the time.
Where is the code that says you have cover the ends of unused conductors?
Fair point.
But whether it is a code requirement or not, I would stick them in a terminal strip to make it look neater and to avoid contact with live conductors or components.
There are no wire nuts listed for use with a single conductor, how are you supposed to deal with that?
These work quite well:
https://www.homelectrical.com/compa...MIpIOQ5bCX1wIVSlqGCh0wtAhEEAQYASABEgIbMvD_BwE
SceneryDriver
110.14(B): ... All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an identified insulating device.
Some amount of tape should satisfy this requirement for small branch circuits. Unused branch circuits...maybe a grey area.
Caution use of terminal blocks that may be considered power distribution blocks (314.28E) - box sizing is different.
Are you talking about the free end of a wire that is still connected to the electrical system at the other end, or in a box at the other end and potentially useable in the future?
Or are you talking about the end of a wire/cable that is completely disconnected and simply being abandoned in the wall?
-Jon