Termination temp

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have DC equipment call it X which draws 350A max.

I have 24x20A fuse factory installed in upstream DC equipment call it Y that feeds the equipment X with feeder cable call it Z.

The feeder cable Z connects to one terminal in equipment Y and other side one terminal on equipment X.

Questions;

1. Can one use NEC 2017 section 110.14(C)(1)(b) to determine temperature termination for the above case? Note above case is DC

2. NEC 2017 section 110.14(C)(1)(b) says to use 75C or higher for termination temp for circuit over 100A. So does this mean their is no 60C termination for circuit over 100A?
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
1. Can one use NEC 2017 section 110.14(C)(1)(b) to determine temperature termination for the above case? Note above case is DC

2. NEC 2017 section 110.14(C)(1)(b) says to use 75C or higher for termination temp for circuit over 100A. So does this mean their is no 60C termination for circuit over 100A?
There's nothing I see that limits the application of 110.14 to AC circuits.
The guidance in 110.14(C) allows us to imply the rating of unmarked terminations based on ampacity and wire size. Maybe there are old terminations out there that are 60C even though they are in a 100A circuit but the NEC assumes they don't exist.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Questions;

1. Can one use NEC 2017 section 110.14(C)(1)(b) to determine temperature termination for the above case? Note above case is DC

2. NEC 2017 section 110.14(C)(1)(b) says to use 75C or higher for termination temp for circuit over 100A. So does this mean their is no 60C termination for circuit over 100A?
Are you trying to use cable with insulation rated for 60°C?
 