1. Are there any pieces of commercial or industrial grade equipment that are only rated 60* C?
2. This question is related to code 110.14(C) and code 250.122(B). Say for a 100A breaker (marked 60/75), I design the wire size to be #1 AWG (110A) from the 60*C column. The specifications state to use THWN wire, so the contractor installs #1 AWG (130A) rated 75*C. Since the minimum wire ampacity should be #3 AWG for 75*C, shouldn't this require the ground to be upsized per 250.122(B)?
This question is in regards to commercial and industrial only. My concern is applying code 110.14(C) for all pieces of equipment 100A and below, especially for new construction. For a renovation project, I might run into electrical equipment that is not marked with a termination temperature rating. For new construction, how often do you see a piece of equipment that is not marked with a termination temperature rating?
2. This question is related to code 110.14(C) and code 250.122(B). Say for a 100A breaker (marked 60/75), I design the wire size to be #1 AWG (110A) from the 60*C column. The specifications state to use THWN wire, so the contractor installs #1 AWG (130A) rated 75*C. Since the minimum wire ampacity should be #3 AWG for 75*C, shouldn't this require the ground to be upsized per 250.122(B)?
This question is in regards to commercial and industrial only. My concern is applying code 110.14(C) for all pieces of equipment 100A and below, especially for new construction. For a renovation project, I might run into electrical equipment that is not marked with a termination temperature rating. For new construction, how often do you see a piece of equipment that is not marked with a termination temperature rating?