I am a design engineer (let the abuse begin). What is the best source of information in advance of the equipment arriving on site to determine equipment termination temperature ratings? I could use 60 deg C on everything, but that seems like overkill and would add additional costs in every design.
Does anyone ever see 60 deg C terminations? Are most terminations 60/75 deg C or 75 deg C?
Any rules of thumb for motor, HVAC, MCCs, panelboards, etc.?
For example, if I planning for packaged heat pump (say Carrier or Trane) and the HVAC designers says that the MCA is 75A. Can I start with the 75 deg C column of Table 310.15(B)(16) or should I start with the 60 deg C column? (Note that a lot of HVAC in water/wastewater plants is on the roof so I would correct for temperature thereafter).
It seems like NEC 110.14 tells us to assume 60 deg C if <=100A and 75 deg C if >100A unless we know more from the manf. Am I reading that correctly?
Any thoughts are appreciated.
Thanks.
Does anyone ever see 60 deg C terminations? Are most terminations 60/75 deg C or 75 deg C?
Any rules of thumb for motor, HVAC, MCCs, panelboards, etc.?
For example, if I planning for packaged heat pump (say Carrier or Trane) and the HVAC designers says that the MCA is 75A. Can I start with the 75 deg C column of Table 310.15(B)(16) or should I start with the 60 deg C column? (Note that a lot of HVAC in water/wastewater plants is on the roof so I would correct for temperature thereafter).