Terminations in Damp locations

Status
Not open for further replies.

Red Wiggler

Senior Member
Can anyone tell me a Code article that references terminations (wire splices) in damp areas? Specifically prohibiting the use of a product such as a wire nut or wago?
 
110.11 maybe.

110.11 Deteriorating Agents. Unless identified for use in
the operating environment, no conductors or equipment
shall be located in damp or wet locations; where exposed to
gases, fumes, vapors, liquids, or other agents that have a
deteriorating effect on the conductors or equipment; or
where exposed to excessive temperatures.
 