Let me explain the reason for my question. First, we should all and always be a bit hesitant to accept any claims of a miracle product, especially if the claims were made by the vendor. In this case, we have an experienced electrician (and now engineer) testifying to the success of one project that used that product. I applaud the sharing of that type of information. But I still find myself being hesitant, because there are things about the product that I do not yet know.
This product appears to cause a very good electrical contact between itself and the ground rod. But the product also must make contact with planet Earth. The function of a ground rod is to provide an electrical path from a point within the electrical distribution system to planet Earth. If cjcrawfo were to tell us that a ?Before and After? series of ground resistance tests were made, and that both the Before and the After used the Fall of Potential Method, my hesitations would be greatly reduced. That specific test uses a probe some great distance from the ground rod (i.e., not in contact with, and indeed well beyond the immediate influence of, the TerraFill product). Considering the distance from the outside of the ground rod to the outside of the hole in which the TerraFill was poured, the probe used by the Fall of Potential Method is at an essentially ?infinite? distance. In other words, it would provide a true picture of the difference in ground resistance that the product was able to achieve.
If some other method had been used to measure ground resistance, I would be interested to find out whether that method had measured not only the resistance of the physical contact between the product and the ground rod, but also the resistance of the combined electrical path formed by the product and the surrounding dirt.
By way of counter-example, suppose a person tried to measure ground resistance by clipping one ohmmeter terminal to the ground rod and the other to a 12 inch metal probe. Suppose that the ?Before? measurement was taken by sticking the 12 inch probe into the dirt 2 inches away from the ground rod. Suppose next that the ?After? measurement was taken by sticking the 12 inch probe the same 2 inches away from the ground rod, but this time that distance caused the probe to go into the product, and not into dirt. I would not be at all surprised if the ground resistance measurement improved significantly. But neither would this convince me of the value of the product.
And so I ask again, how were the ground resistance measurements taken?