I would assume a 32A mobile plug-in charger wouldn't need more than a 40A breaker, based on the code. Yet despite already being +25% per code at 40A for continuous load, Tesla is recommending to bump that another +25% to 50A. I can't really tell if this is a manufacturer requirement or a recommendation based on this link of theirs. What are your esteemed thoughts on this? For a short run, it makes like 5% cost difference, but for a 40+ ft run it would be a serious cost increase.
Is it required per this language (and I guess then NEC would say follow the manufacturer)? Would you do so if it wasn't a hard requirement?