Grouch
Senior Member
- Location
- New York, NY
Hey guys,
I attached an abbreviated version of the cutsheet for one of Tesla's car chargers.
Page 2 mentions the charger connects to a single phase, 200-240 volt power supply.
Page 3 mentions that with a 60 amp breaker, the charger can draw 48 amps at 240 volts... for a power output of 11.5 KW.
For a load such as this, what happens to the current and power output if you connect to a 208 volt panel?
For a resistive load, both power and current decrease with a voltage decrease; for a motor load, current increases and power remains the same with a voltage decrease. How do you analyze this type of load?