CustomElectricLLC
Member
- Location
- Midlothian Texas
- Occupation
- Electrical Contractor
Doing load calculations for a service where a client wants a Tesla power connector charger installed. Service is 200A w/ a 2, 3, and 5 ton unit ac/heat pump units with 5-10kw heat strips in AHU's and is roughly 4k sq ft. I ran all the numbers and with standard method Im slightly above 200 amps (208 amps I believe). Its a rough guesstimate because I can't go through everything in the whole house but definitely most concerning loads are all those heat pumps units on such a smaller service size. I figured the EV charger at 100% in my load calcs but the customer also has Tesla solar and (2-3) power wall units. Looking at the specs to PW units have a 11kw resistive/98A LRA max or ≤32A RLA output (for motors) capability. Can anyone shed some light on if I can figure this extra available capacity into the load calculation and perhaps be in the green for the install? First time I ran into something like this. Had it not been for the power wall Id tell customer he needs a service upgrade period. Thank you